ONAN 8500 TRIPS WHEN I TURN ON 1 AC UNIT

Onan 8500 generator trips after starting 1 of 2 ac units, units run ok on shore power, has 9500 hrs. also have to use aux power when starting.
Thanks for any help

John

3 Replies

  • i think a weak breaker is less likely than the things i mentioned
    although it is possible

    50amp shore power is 50*120*2 = 12000 watts
    50% more power than the generator

    i think you have a problem on one genny line

    two many items, or something that is failing,
  • Mr. Wizard Thank you going to rv tomorrow, will give it a shot how about a weak breaker on onan.

    Thanks John
  • aux power when starting the Onan ?

    if so sounds like a 'house battery' problem

    only (1) particular a/c causes the Onan to trip ?

    overload alarm or trip the breaker

    could be the converter and the a/c are on the same generator leg (line 1 or line 2)

    heavy charge load combined with a/c startup load 'bingo' too much load

    and/or that a/c needs a new start capacitor for the compressor

    start by checking the batteries, and cables, then turn off the circuit breaker for the converter and try to start that a/c