Cummins12V98 wrote:
Bobbo wrote:
I agree. If you are going to run 4 wires, install the outlet and breaker that takes all 4 wires. Done once and finished.
That is what I did. I have a 30 amp RV. For now. When I ran my power, I pulled three 6g wires (black, red, white) and one 10g wire (green), put in a 50 amp breaker, and a box with 50amp/30amp/20ampGFCI outlets and breakers. I will never have to touch that wiring again, no matter what I may buy in the future. It did not cost THAT much more to do than a straight 30 amp setup would have been.
(While doing this, I also ran a second conduit and installed a separate box with telephone line and satellite/cable coax. Like I said, done once and finished.)
I am curious, you say "I pulled three 6g wires (black, red, white) and one 10g wire (green), put in a 50 amp breaker, and a box with 50amp/30amp/20ampGFCI outlets and breakers" is that code compliant? Potentially you could have 100A drawing on that one 50A breaker in the panel if you had all three receptacles being used at the same time. I know that is unlikely, but is it code?
As long as the breaker in the main box is sized to the wires, yes, it is code compliant. Anything over 50 amps, total, on either leg will trip both legs and kill the power.
Think about all of the 15 amp outlets in your home on a single 15 amp or 20 amp breaker. Add them all up and they grossly exceed the rating of the breaker.
And, actually, if I was pulling 50 amps on both legs of the 50 amp outlet, 30 amps on the 30 amp outlet, and 20 amps on the 20 amp outlet, I would be pulling 150 amps! It would be 80 amps on one leg and 70 amps on the other.