Your propane regulator is sized (btu flow) to allow ALL OEM propane appliances to be fully operated...fridge on propane, water heater on propane, stove top burners on, oven on, furnace on.
Regulators should be set to maintain 11" WC with 100% of propane equipment in service (although 50% will work).
Sounds like your LP regulator is NOT working correctly.....could try to adjust it but may just want to replace.
Regulators should be set to maintain 11" WC with 100% of propane equipment in service (although 50% will work).
Sounds like your LP regulator is NOT working correctly.....could try to adjust it but may just want to replace.