Gjac wrote:Old-Biscuit wrote:This is a photo of my Gauge, the OM calls it a Mamometer gauge and as long as it is in the green it is good. If you look close it is not measured in ins of HG or WC the units are oz/sq in.Gjac wrote:
I have noticed that if my refer, HWH, and stove is on propane and the furnace kicks in the stove flame gets very lazy and yellow. I have a gauge that tells me that my propane pressure is good.
What kind of gauge?
11" WC is roughly 0.4 psi
Nice gauge.......fairly accurate means of measurement.
16 oz/sq. in equals 1 PSI
11 inches of water column or about 6.3 oz/sq.in (that's about 0.4 psi).
IF stove flames get lazy/yellow with those other appliances in service on propane then your LP Regulator is NOT keeping up with demand. May need adjusted or replaced....it should maintain 11" WC with 100% of appliances in service.
On Edit: The 'Green' scale-------5.5 to 8 oz/sq. in equals 9.5 to 14" WC.
9.5" WC is what LP Regulator should maintain at full flow......but is too low for proper operation of furnace, water heater & fridge.
At 10" WC....they will have issues lighting off, maintaining flame and not enough btus being released for good heat transfer.