routeforty wrote:
Thanks to everyone for the responses. I think I will need to run a 2" conduit with #10,8,&6 wire for what ever the current or future needs may be ;). Just kidding-was hoping(dreaming) I could get by with 10 wire, but have decided to go with 6. Don't plan on ever needing 50amp, as we just bought a new Class C, and neither I or DW care for class As, but who knows what the future holds. A 125' roll of 6 wire is only about $50 more at Lowes than 8-I just hate to work with wire that big :( . Next question is-this will all be under concrete, so could it lay on top of the ground(the conduit with wire inside)and pour the slab on top of it or should I dig a small trench to put it in. Gary
Q. What is the minimum depth for placing Schedule 40 PVC conduit below a concrete slab?
A. If it's under a building, there is no depth requirement. If it's placed outside under a concrete slab, then the minimum cover is 4 inches Table 300.5 National Electrical Code.