Artum Snowbird wrote:
With most things power wise, it seems prudent to put in a lot more wire size instead of just enough. Now, for example, if you put in enough for 50 amps and your circuit breaker is only 30, you will be comfortable knowing that if a shop comes off the side, or a welding plug, a freezer, or anything else that might take a steady load, you can put in a sub panel out there and still have your 30 to run the rig happily.
Maybe even going the extra now to put in a panel and then drop to a 30 amp plug might make sense.
Copper cable is expensive and larger sizes get very expensive. If the OP is installing conduit, it will be easy to pull a larger cable if he needs it later...plus a 50amp RV has 4 conductors not 3, so he still needs to pull cable in the future.
Don't forget to add the 30' for the RV cable to get from the outlet into the RV breaker box.
Plug your numbers into a voltage drop calculator and it will spit out the answer. Probably a good idea to check the available voltage first.
- If your house panel is starting around 120v, a 5% drop means your outlet will have 114v power. Above 110v is usually fine.
- If you house panel is marginal and only has 110v, a 5% drop means you are feeding a marginal 104.5v into the RV.
Another question, no one asked is what do you plan to run? If you won't be running the air/con, you can probably just run a 15-20amp line. You are limiting yourself but if you never plan to run any high amp appliances, why waste the money.