joe0508
Feb 24, 2014Explorer
rv furnace
I have a hydro flame furnace.I have been having a problem when heating my motorhome.The furnace will heat the motorhome until it reaches the temperature the thermostat is set for than the burner will ...
enblethen wrote:It works as it should with the cover off but with the cover on the blower will kick on as it should than after 5 to 7 sec later the burner will kick in heating the rv.Than the burner will kick off as it should but the blower never stops with no sign of the burner kicking back on.No matter how cold the rv gets.With the cover on the anticipator doesn't open but with it off it does.I think this has something to do with the blower never shutting off.
Remove the cover from the thermostat. Depending on the model there is two styles of anticipator. One is a bar with a small arm. The arm needs to be about .8. The other style is a small disc with a small screwdriver slot. Turn the arrow to about .8.
I doubt this is the problem unless the coil is open.
Did you try connecting the wires together?