350w at 230v is only 1.5 amps
6000btu of heat would take about 1600w of electrical energy to produce
Not sure how much electrical energy it would take to remove 6000 BTU of heat, but I'm reasonably sure that 350w is not enough , unless that is one super efficient heat pump, not a freon refrigeration cooling unit
https://www.mhiaa.com.au/index.php/component/mitsubishi/products/default/96
The Daikin Uluru Sahara 7 is 8500BTU for 430W input , 20.3 EER. It uses r32 refrigerant. (not available in the USA), found in australia
There is a Daikin 230 volt unit that I think you can buy in the US that is 590 watts at 9000 btus, So imagine less at 6000 btu, maybe 450 watts?