If it's an Atwood combo water heater it has a dual ON/OFF Panel with Light in between switches.
Like this

That Light is a 'Fault' indicator light
It will come on when heating with propane IF:
Propane fails to light
Propane normal t-stat fails to open and the ECO (high temp t-stat) opens
It will also come on when heating with electric IF:
ECO (high temp t-stat) opens cause normal t-stat failed
Atwood uses the same set of t-stats for both electric and propane operation
Normal pre-set to Open at 140*F (re-closes when temp drops to 110*F)
ECO pre-set to Open at 180*F (re-closes when temp drops below 150*F)
IF ECO has opened.fault light ON water heater will not reheat again until fault light is cleared (water temp low enough/problem with propane not lighting) and ON/OFF switch turned OFF then back ON
Sounds like you need a new normal t-stat.
Normal & ECO t-stats are sold together as a set ($15-$18) and should change both.
Electric heating element is feed from a 110V AC circuit breaker..........but DC power is used to activate the 110V AC to element.
DC power from DC Dist. Panel (fuse) goes to ON/OFF switch (both electric and gas) then to a relay. When relay closes AC power then goes from Circuit breaker to element.
Electric element and relay are on backside of water heater tank (inside rv) under protective cover.
T-stat and ECO are in outside compartment under a foam cover.
Brown wires are on normal temp t-stat
Red wires on ECO
Also should be a thermo-fuse (brown wire with clear plastic tube---goes from circuit board to t-stat)
It melts if gas flame blows back out of combustion chamber (190*F). One time device-----cuts DC power
Like this
That Light is a 'Fault' indicator light
It will come on when heating with propane IF:
Propane fails to light
Propane normal t-stat fails to open and the ECO (high temp t-stat) opens
It will also come on when heating with electric IF:
ECO (high temp t-stat) opens cause normal t-stat failed
Atwood uses the same set of t-stats for both electric and propane operation
Normal pre-set to Open at 140*F (re-closes when temp drops to 110*F)
ECO pre-set to Open at 180*F (re-closes when temp drops below 150*F)
IF ECO has opened.fault light ON water heater will not reheat again until fault light is cleared (water temp low enough/problem with propane not lighting) and ON/OFF switch turned OFF then back ON
Sounds like you need a new normal t-stat.
Normal & ECO t-stats are sold together as a set ($15-$18) and should change both.
Electric heating element is feed from a 110V AC circuit breaker..........but DC power is used to activate the 110V AC to element.
DC power from DC Dist. Panel (fuse) goes to ON/OFF switch (both electric and gas) then to a relay. When relay closes AC power then goes from Circuit breaker to element.
Electric element and relay are on backside of water heater tank (inside rv) under protective cover.
T-stat and ECO are in outside compartment under a foam cover.
Brown wires are on normal temp t-stat
Red wires on ECO
Also should be a thermo-fuse (brown wire with clear plastic tube---goes from circuit board to t-stat)
It melts if gas flame blows back out of combustion chamber (190*F). One time device-----cuts DC power