Here's a Battery/Coil/Points/Condenser Ignition.
With Points Open and Condenser disconnected, you should see Battery Voltage on both sides of the Coil.
When Points CLOSE, a Magnetic Field forms in the Coil.
Spark Occurs when Points OPEN and the Magnetic Field suddenly collapses.
You can see from the Diagram that if the Condenser has failed Shorted, it will be as if the Points never Open.
I can't tell you the electronic theory, but I understand that if the Condenser is failed Open (not charging when the Points Open, as if it wasn't even there), the Magnetic Field will not collapse quickly enough to cause an adequate Spark. Perhaps no Spark at all.
From what I've seen, many of the "Safeties" on a genset are bypassed when it's cranking. If it fires up, then quits as soon as you release the switch from Start, then it's possible a Safety like Oil Pressure or Power Output isn't being satisfied. Our BFA, for example, used House Battery Voltage to Crank, Provide Ignition, and run Fuel Pump when the switch was in Start. Once it started and I released the switch to Run, it provided its own 12VDC for Fuel, Ignition, and recharging the Battery. If it didn't produce 12VDC it'd stop. Oil Pressure Switch was also bypassed.
Check your Service Manual. Find the Wiring Diagram. I think you'll find that the "Switch" in the diagram above is actually a multi-contact switch and/or the output of a Relay or two.
I'm gonna guess that you have a control inside the Coach as well as on the Genset itself. Sometimes problems arise with the inside control and/or the wiring and connections to the Genset. Try disconnecting the inside control.