PWM, 12v charging, 12v panels in parallel.
PWM, 24v charging, 12v panels in series.
There are a couple of pages of various batteries listed by make and model numbers with the appropriate specs for each.
yes, the abs V, float V and IUI is based on battery brand/type and other stuff is based on capacity/type. No need to try and find/program battery charging specs for listed batteries.
You've bought into bogart's engineering, others buy into their own or experiment or other's or even WFCO, go for it.
TABLE 4: Programmed values for each P22 charging profile number. See *NOTE below
All values are normalized to a “capacity” of 220Ahr. After placing a profile in P22, then change the P3
setting to your value unless your system has capacity=220 Amp hr.
Battery type
( with total system volts not battery volts)
Profilenumber P22 P1 AbsorbV P2AmpssetptP3capacityAhr P14Timehr P15highVP16floatVP20OverchargeP21Finihamps
"Generic" wet cell (12V) 1 14.4V 2.0% 220AH 4.0h 15.7 13.2 10% 3.0%
"Generic" wet cell (24V) 2 28.8 2.0% 220AH 4.0h 31.4 26.4 10% 3.0%
Trojan wet cell (12V) 3 14.4V 2.0% 220AH 4.0h 16.2V 13.4 10% 3.0%
Trojan wet cell(24V) 4 28.8V 2.0% 220AH 4.0h 32.4V 26.8 10% 3.0%
Crown wet cell(12V) 5 14.5V 2.0% 220AH 4.0h 15.9 13.5 10% 3.5%
Crown wet cell(24V) 6 29.0 V 2.0% 220AH 4.0h 31.8 27.0 10% 3.5%
US Battery(12V) 7 14.8V 2.0% 220AH 4.0h 15.5 13.0 15% 3.5%
US Battery(24V) 8 29.6 V 2.0% 220AH 4.0h 31.0 26.0 15% 3.5%
Concorde AGM(12V) 9 14.3 V 2.0% 220AH 4.0h 16.5 13.3 7% 2.0%
Concorde AGM(24V) 10 28.6 V 2.0% 220AH 4.0h 33.0 26.6 7% 2.0%
Deka monobloc(12V) 8A, 8G 11 14.2 V 2.0% 220AH 8.0h 14.2 13.5 20% 5.0%
Deka monobloc (24V) 8A, 8G 12 28.4 V 2.0% 220AH 8.0h 28.4 27.0 20% 5.0%
Interstate(12V) wet cell 13 14.5 V 2.0% 220AH 4.0h 15.3 13.4 15% 4.0%
Interstate(24V) wet cell 14 29.0 V 2.0% 220AH 4.0h 30.6 26.8 15% 4.0%
GNB-Absolyte(12V) VRLA 15 14.3 V 1.0% 220AH 8.0h 14.3 13.5 7% 2.0%
GNB-Absolyte(24V) VRLA 16 28.6 V 1.0% 220AH 8.0h 28.6 27.0 7% 2.0%
Generic-Wet Cell-no hi volt finish 17 14.7 2.0% 220AH 4.0h 15.0 13.2 12% 0FF
Generic-AGM-no hi volt finish 18 14.3 2.0% 220AH 4.0h 15.0 13.3 7% 0FF