Something sounds funny!
It should be minimum 10 gauge wire for 30 amp. NEC requires 310 for 30 amp.
The AC unit should not be running directly off genset.
The genset should go through a transfer switch or on some rigs a receptacle where the shore power cord plugs in.
It then should go to a 120 volt power distribution panel. There a 20 amp breaker would feed the AC unit on #12 wire.
Onan only wire what is inside the genset. Connection to the rig is done by the rig's manufacturer. I would be checking with them!