30 amp motor home plug has one hot leg, one neutral and a ground. A 50 amp plug has 4, 2 hot legs, a neutral and a ground.
When you have a dog bone style adapter, 30 at the pedestal to the 50 amp motor home plug, are both hot legs on the 50 amp side wired with the one hot from the 30 amp plug?
Another related question; I have a voltage regulator rated for 50 amps. using a 30 amp plug at the pedestal to the regulator "in" side which has a ground, neutral and hot leg position.
The "out" going positions are similar to the "in" with only 3 positions however the 3 wires coming out must wire a 4 position 50 amp plug (the power cord from the motor home) Conversely, the 4 wire 50 amp cord must be wired into the 3 position regulator.
Question, which wire from the 4 wire cord is left out? I'm leaning toward putting both "hot" wires from the cord on the one "hot" position on the "out" side of the regulator.
Now I did this before without a question as I cut a dog bone in half and used both ends to hook up the regulator. This time wanting to improve the set up, I have used 30 amp 3 wire, and 50 amp 4 wire with appropriate reusable plug ends.
Thanks very much. Tom
When you have a dog bone style adapter, 30 at the pedestal to the 50 amp motor home plug, are both hot legs on the 50 amp side wired with the one hot from the 30 amp plug?
Another related question; I have a voltage regulator rated for 50 amps. using a 30 amp plug at the pedestal to the regulator "in" side which has a ground, neutral and hot leg position.
The "out" going positions are similar to the "in" with only 3 positions however the 3 wires coming out must wire a 4 position 50 amp plug (the power cord from the motor home) Conversely, the 4 wire 50 amp cord must be wired into the 3 position regulator.
Question, which wire from the 4 wire cord is left out? I'm leaning toward putting both "hot" wires from the cord on the one "hot" position on the "out" side of the regulator.
Now I did this before without a question as I cut a dog bone in half and used both ends to hook up the regulator. This time wanting to improve the set up, I have used 30 amp 3 wire, and 50 amp 4 wire with appropriate reusable plug ends.
Thanks very much. Tom