Hi,
I maintained 875 amp-hours of battery bank with a 40 amp PD converter. Unless you boondock LOTS the extra 15 amps won't give much benefit on a twin twelve volt system. About 85% state of charge acceptance rate is 12.5 amps per 100 amp-hours of storage.
If you are serious about boondocking look at a decent solar system.
I maintained 875 amp-hours of battery bank with a 40 amp PD converter. Unless you boondock LOTS the extra 15 amps won't give much benefit on a twin twelve volt system. About 85% state of charge acceptance rate is 12.5 amps per 100 amp-hours of storage.
If you are serious about boondocking look at a decent solar system.