TXiceman's avatar
TXiceman
Explorer II
Feb 09, 2017
50 amp electrical issue
I have a strange issue going on with the power. I have a 50 amp RV with a Progressive Industries EMS and also a Hughes Auto Transformer when needed.
As long as the campground does not have many campers (this is on the 30 amp loop, but we have "50 amp" service), we do OK to a point and I have to use the Auto Transformer so that we can run the heat pumps or A/C. We are southwest of Houston, so we get really mixed weather.
Now the problem. Without the Auto Transformer, L1 will drop voltage as low as 104 volts which shuts down the EMS. When L1 leg goes low, L2 goes high to about 127 volts with no or a very small load on L2. The EMS drops the trailer off line with L1 low voltage.
If I put the Auto Transformer on line, L1 will drop with a 20 amp load and it will boost the voltage on L1 to keep the voltage up. Then L2 will go high and the EMS will take the trailer off line on high voltage on L2.
With no or 3 or 4 amp load, both legs will read 121 volts. Add some load and the voltage drops like a rock. I had the park check the pedestal and everything is OK there. I checked all of the connections in the RV and all is tight.
The park flooded twice last year and the electrical was under water for 2 or 3 weeks. They closed the park and pulled the guts in all of the panels and replaced them after the water went down.
I am at a loss to solve the problem and the park is no help. We are hosting here until the end of March but maybe forced to leave early if they can not get us dependable power. The trailer has a 22 cubic foot residential refrigerator, washer drier, dishwasher and two heat pumps. All appliances are pulling normal amps when at voltage.
Any ideas to pass along would be appreciated.
Ken
  • TXiceman wrote:
    Jerry, that is my thinking since they do not know the condition from the flood. They do not have any way to high pot test the wiring. Trying to get the state park to get an electrician out to check it.
    Ken
    That's a good idea to have electrician come out. Make sure he understands fully what is going on.
    Testing the pedestal voltage under load is the best way.
    Another is to completely disconnect that branch circuit from the main panel then OHM out all wires involved. Hi pot would be best. Should be no continuity between the 4 conductors.
    keep us posted.
    Good thing you had EMS. I use the same one too.
    My neighbor had some serious damage once. He didn't have one.
    Jerry
    Ps. I've troubleshot and repaired underground problems in the past.
    You never know what you might find.
  • What the OP describes is an imbalance between the two legs of service that only happens when using the Hughes unit. The statement that he is unable to run an A/C or heat pump without the transformer is more telling than anything else since that should be easily accomplished with good service to the pedestal.
    I wouldn't want to sit connected to a service that sagged to 104V under a typical oad. Your EMS is saving your bacon with that situation. My guess is that the campground has a problem with their campground "grid" and I wouldn't be looking for a quick solution to the problem. Sorry for the negative post on my part but you have all the good gear to camp with adequate or typical electric service and that isn't' being provided.
  • MrWizard wrote:
    do you have true 50amp service
    or do you mean you have 30+20 ?
    are you on a 30amp with adapter and where is the autoformer in this circuit
    30a ped > autoformer > EMS is the correct setup
    you can not parallel this with a 20amp on the other leg
    total imbalance in the circuits will occur
    Agree - in a situation like this accuracy is critical as one can't sort out a problem if isn't clearly described and therefore understood. That aside, since the OP is using a Progressive Industries EMS I'd suggest he call them to see if there's anything they can offer to help sort this out.
  • do you have true 50amp service
    What does this mean? Is the pedestal 30a? I assume autoformer, EMS and RV are 50 amp.
    Or as host do you have 50a and the rest are 30?
    There is only L1 with 30a service so the L1 vs L2 seems confusing unless that is just your RV.
    Are you using adapters?
    Otherwise yes whenever voltage climbs it is pointing to a bad neutral.
    Could check voltages at all boxes in the loop to possibly determine where the issue starts. Or you may end up back at the main panel.
  • Jerry, that is my thinking since they do not know the condition from the flood. They do not have any way to high pot test the wiring. Trying to get the state park to get an electrician out to check it.
    Ken
Having RV issues? Connect with others who have been in your shoes.24,350 PostsLatest Activity: Jan 17, 2026