DrewE
Apr 06, 2020Explorer III
avarusbrightfyre wrote:
Wouldn't increasing to 24 or 48 volts require more batteries to reach the same capacity? I believe I would need twice number the batteries at 24 volts to get the same number of amp hours as a 12 volt setup. I plan on mounting the inverter right next to the batteries and using big fat cables to minimize heat.
You do need twice as many batteries to have the same charge capacity (measured in Amp-hours). You do not need twice as many batteries to have the same energy storage (measured in watt-hours), and it's energy that you're ultimately using. Since the voltage to the inverter is greater, the current it requires for the same output is proportionally lower, and so your amp-hour requirements--but not your watt-hour requirements--are also correspondingly lower.
Incidentally, this is basically the same reason why power company distribution lines operate at high voltages: they need to carry much lower currents to supply the same amount of power, and so they can use reasonably sized wires and still have acceptably low line losses.