Bumpyroad wrote:
ken white wrote:
Bumpyroad wrote:
what is "reverse polarity" on a 50 amp outlet? I can see on a 30 amper where the hot and neutral could be reversed, but on a 50 amp outlet if one of the hots was switched with the neutral making the neutral hot, you would have a hot to hot connection???????? wouldn't that be sort of a "mess"?
bumpy
No different than at your house where you typically have a 240 VAC service entrance with 2 - 120 VAC branches out of phase.
The transformer secondary acts as a voltage source and unless the 2 hots are shorted together, there won't be an issue.
EDIT: Poor spelling... :(
that still does not clarify it. in 50 amp hookup, you normally have two hots and a neutral (ignoring ground) if anything is hooked up wrong you have two hots together, they are shorted together and should be an issue.
bumpy
bumpy, it is no different than a branch in your house having this issue...
The pedestal is just a 4-wire branch circuit, and in this installation, the wires were connected to the wrong terminals.
If the 2 hot wires were out of phase, then 240 VAC would be applied to a 120 VAC branch and all of the smoke would be let out.
If the 2 hot wires were in phase, the device under load would see a zero voltage difference in potential. EDIT: This occurs when the campground wires a 30 amp service into a 50 amp service socket - fake setup...
Without knowing exactly what occurred, all we can do is speculate.