3_tons
Jun 22, 2019Explorer III
Haycamper wrote:
3 Tons
The autoformer increases the output voltage but it doesn't increase the output power so the output current actually drops. The autoformer input current goes up when the input line voltage drops. So even though the output current may be 28 amps, the input current could be over 30 amps. The increase in voltage is not free it's not a power station where you can just turn up the boiler
“The autoformer increases the output voltage but it doesn't increase the output power so the output current actually drops”...
Isn’t this rather self evident, but you dismiss the fact that the ‘power factor’ is corrected to near unity thus the air conditioner sees no (or minor) voltage sag...It’s this voltage sag that can burn out compressor windings...
“The autoformer input current goes up when the input line voltage drops. So even though the output current may be 28 amps, the input current could be over 30 amps. The increase in voltage is not free it's not a power station where you can just turn up the boiler”...
I know of no single rooftop air conditioner that uses that many amps, but thats just me with my smallish truck camper - quite naturally outliers do exist (especially when only on a 30a pedestal) when running multiple appliances, high ambient temps, etc....This is exactly where one should instead opt for a 50a pedestal... Judgement plays a large role here...
BTW, recall that your OP question was in reference to a 20a breaker - just saying...
Having RV issues? Connect with others who have been in your shoes.24,404 PostsLatest Activity: Aug 06, 2026