AGM Adventures- Update
Updated 31 Jan 17
Initial results. I will re-test the AGM after it does one deep cycle to confirm these results.
EDIT completed 6 Oct
Test was to put the test battery as the only battery running the 5er, and whole house with the inverter to run a kettle and then a toaster, measuring initial voltage sag and noting the amps draw.
The AGM is brand new out of the box
http://www.hespv.ca/hesproductspecs/HES/Stark_Battery_TD_ENG.pdf
Out of the box voltage was 12.82. Dated July this year (I think) did an initial charge and left overnight voltage today 12.89 very slowly still going down--can't wait, do the tests!
Used the Trimetric which is only to one decimal point, so that can throw things off some, but anyway, this is how it came out.
First the AGM showed 12.9 on the Trimetric, turned on inverter and bam, voltage dropped to 12.6 with a 1.1 amp draw (no inverter load yet) voltage still falling fast got to 12.2 !!! so turned on toaster voltage dropped to 11.2, turned off toaster, voltage bounced right back to 12.6 with inverter still on.
Seems the battery needed a kick? Waited for things to settle, still 12.6v so ran kettle. Voltage 10.9 with 93.4 amps draw. Unplugged kettle, voltage right back to 12.6 inverter off 12.7 !
Anyway results seem to be ( new 100AH AGM)
A. Toaster- 1 volt sag with 75 amps draw
B Kettle= 1.7 volt sag with 93 amps draw
However, something funny might be going on with the battery not up to speed yet, so will try again after taking it down to 50% and recharging. Not sure when that will get done.
Meanwhile, for comparison I did the same test with one 5 yr old T-1275 that spent its first 2 years in a golf cart then I have been working it hard off and on but also trying to take care of it for the last three years. SGs are all in the green, capacity tested recently as about 135AH out of 150AH rated. Battery full going into the test.
A. Toaster- 1.2v sag with 71 amps draw
B. Kettle- 1.5v sag with 93 amps draw
With my usual 6 battery bank in the 5er (two T-1275s and four 6s)I got
A. Toaster- 0.5 volt sag with 66 amp draw
B. Kettle- 0.6 volt sag with 84 amp draw.
I don't know why the same inverter with the same loads has different (fewer) amps draw from the 6 battery bank. Most of the wiring is the same.
(I will not be able to report when amps begin to taper with the AGM vs a Wet like PT wanted to know, because I have to use my Vector charger which has its own taper time. I would need two of these AGMs to use my charger that could show that for PT due to the 27a charging limit on the one.)
I don't know what is normal for a brand new AGM not been cycled yet, so I will do a deep cycle and then see what it behaves like after that.
Initial results. I will re-test the AGM after it does one deep cycle to confirm these results.
EDIT completed 6 Oct
Test was to put the test battery as the only battery running the 5er, and whole house with the inverter to run a kettle and then a toaster, measuring initial voltage sag and noting the amps draw.
The AGM is brand new out of the box
http://www.hespv.ca/hesproductspecs/HES/Stark_Battery_TD_ENG.pdf
Out of the box voltage was 12.82. Dated July this year (I think) did an initial charge and left overnight voltage today 12.89 very slowly still going down--can't wait, do the tests!
Used the Trimetric which is only to one decimal point, so that can throw things off some, but anyway, this is how it came out.
First the AGM showed 12.9 on the Trimetric, turned on inverter and bam, voltage dropped to 12.6 with a 1.1 amp draw (no inverter load yet) voltage still falling fast got to 12.2 !!! so turned on toaster voltage dropped to 11.2, turned off toaster, voltage bounced right back to 12.6 with inverter still on.
Seems the battery needed a kick? Waited for things to settle, still 12.6v so ran kettle. Voltage 10.9 with 93.4 amps draw. Unplugged kettle, voltage right back to 12.6 inverter off 12.7 !
Anyway results seem to be ( new 100AH AGM)
A. Toaster- 1 volt sag with 75 amps draw
B Kettle= 1.7 volt sag with 93 amps draw
However, something funny might be going on with the battery not up to speed yet, so will try again after taking it down to 50% and recharging. Not sure when that will get done.
Meanwhile, for comparison I did the same test with one 5 yr old T-1275 that spent its first 2 years in a golf cart then I have been working it hard off and on but also trying to take care of it for the last three years. SGs are all in the green, capacity tested recently as about 135AH out of 150AH rated. Battery full going into the test.
A. Toaster- 1.2v sag with 71 amps draw
B. Kettle- 1.5v sag with 93 amps draw
With my usual 6 battery bank in the 5er (two T-1275s and four 6s)I got
A. Toaster- 0.5 volt sag with 66 amp draw
B. Kettle- 0.6 volt sag with 84 amp draw.
I don't know why the same inverter with the same loads has different (fewer) amps draw from the 6 battery bank. Most of the wiring is the same.
(I will not be able to report when amps begin to taper with the AGM vs a Wet like PT wanted to know, because I have to use my Vector charger which has its own taper time. I would need two of these AGMs to use my charger that could show that for PT due to the 27a charging limit on the one.)
I don't know what is normal for a brand new AGM not been cycled yet, so I will do a deep cycle and then see what it behaves like after that.