Am I asking to much from 2x T105's?

I posted a month or so ago about my new solar install, and some issues I was having with the low voltage alarm on my Xantrek 2000W Prowatt while running my coffee maker (Tassimo). I was able to check a little closer this time with a DMM, and confirmed that the E01 alarm (low I/P voltage) was coming on around 10.8V (not over 11 as originally thought)- although it was a little hard to hold the probes which running the coffee maker- either way, I think the inverter is working as expected (I think).

My question, is should 2x T105's be able to handle a 100-125A load for a minute or 2? I'm running 2/0 AWG, 2-3 ft in length. The batteries are on the 3rd season. I don't have much room on the tung of my HTT, but can probably get 4x T105's.

I'm not planning any changes this year, but in the spring may make the change. The microwave also sets off the low voltage alarm.

Thanks in advance
Marc