A fuse isn't always the same rating as the wire. Sometimes a fuse rating can be higher than the wire in the circuit, as in the case of motor circuits like stab. jacks and slides. And sometimes a fuse can be smaller than the wire if voltage drop is an issue.
A fuse "blows" because the element melts from heat. Heat, in watts, is dependent on the amps flowing through the fuse and the voltage drop across it as per Ohms law. The resistance of an element in a fuse is normally dependent on the voltage rating of the circuit.
However, sometimes the voltage rating of a fuse is not linked to the circuit voltage. A fuse voltage rating can sometimes relate to it's ability to extinguish the arc that is generated as the fuse element melts under fault conditions and the type of circuit it is in. A fuse in series with an inductive circuit can have voltages several times greater than the supply voltage during the time it is clearing the circuit and needs to be rated according.
Choosing the right fuse for a specific application can require a range of factors to be assessed such as let-through current rating and speed rating. Time-current characteristics are sometimes important like the graph below that shows an example of a 10 amp "littlefuse". And sometimes a fuse has to coordinate correctly in conjunction with a circuit breaker.
In summary, if a blade fuse in your converter panel blows, simply replace it with the same size. :)