BFL13 wrote:
Thanks. So just live with it as is I guess. The 0.2v drop doesn't matter except when the batts are low and running an inverter load gets the voltage near the low voltage alarm. Then the furnace comes on and pushes it over the edge. Have to shut the furnace off until the inverter job is done.
The 8 amps doesn't matter except when the generator is on to charge the batteries. 75 amps charging drops to 67 amps every time the furnace comes on, which adds to gen running time. Same idea, you can shut off the furnace, but then pay the price after the batts are charged in more furnace time eating the AH you just put in to reheat the RV.
I suppose the LFP guys like their furnace fans spinning faster due to the higher voltages they run at.
I measure voltage drop by seeing it drop on the Trimetric monitor as soon as the furnace comes on. Right after the furnace shuts off, the voltage comes back up part way and then up more only slowly.
Couple of issues at play.
Your monitoring the voltage at your Trimetric connection, that voltage is not the same everywhere depending on wire ga and current draw of the loads combined.
Your inverter when loaded heavy presents a very high current draw and depending on how much wire resistance and load the voltage and current from your power sources may not distribute evenly.
Depending on your current battery bank setup, the wire gauges used and the loads your batteries and converter may not be robust enough to handle all the loads which sends you inverter into low voltage alarm or shut down.
To minimize the inverter low voltage alarm or shut down, one should use the largest wire ga possible that will connect to your inverter terminals and keep the runs (negative and positive combined) as short as possible (reduces the voltage drop the inverter sees).
Has nothing to do with your furnace wiring and more to do with the wiring to the inverter and size of battery bank for the loads presented.
Measure the voltage at the battery terminals and at the inverter terminals with your heavy 120V load, you want to see very little voltage drop between battery and inverter..
You might also wish to check the voltage drop between the converter and batteries, often factory wiring is just good enough to make it charge but upsizing the wire could deliver a bit more voltage and charge current to the batteries..