DFord
Mar 02, 2016Explorer
So far, I've seen no indication that anyone has any idea of why the furnace is short cycling when it should be off. I've given a suggested procedure to begin troubleshooting but everyone just wants to swap parts. All the parts changed out so far has just been a waste of money and nothing has been accomplished.
I've studied the wiring diagram and see the thermostat only has two wires going to it. When the thermostat calls for heat, those two wires are connected. When it's not, those wire are disconnected. Until you know why the furnace is short cycling, the reason for the breaker tripping is a secondary symptom of the actual problem. A bad blower motor could not possibly cause the furnace to short cycle.
I would disconnect the thermostat and use a jumper to run the furnace for a couple of minutes. Then remove the jumper and see what happens. The furnace should not reignite again. What we need to know is if the thermostat is causing the furnace to short cycle. The OP stated the furnace reignited when it was short cycling. If that's the case, the thermostat is the cause of the problem. If only the blower is short cycling, the problem is probably the "relay."
I've studied the wiring diagram and see the thermostat only has two wires going to it. When the thermostat calls for heat, those two wires are connected. When it's not, those wire are disconnected. Until you know why the furnace is short cycling, the reason for the breaker tripping is a secondary symptom of the actual problem. A bad blower motor could not possibly cause the furnace to short cycle.
I would disconnect the thermostat and use a jumper to run the furnace for a couple of minutes. Then remove the jumper and see what happens. The furnace should not reignite again. What we need to know is if the thermostat is causing the furnace to short cycle. The OP stated the furnace reignited when it was short cycling. If that's the case, the thermostat is the cause of the problem. If only the blower is short cycling, the problem is probably the "relay."
"RELAY" description from the furnace manual wrote: