smkettner wrote:
What is the programmed absorption voltage set point?
Exactly where are the measured points? Battery terminals and controller output terminals?
You have the battery sense wires connected? Are you reading voltage on these? what end?
All these reading are off the remote TS45 panel. I assume the battery voltage of 14.54 volts is at the controller output. And the 14.45 is at the batteries post thru the remote sensor line to the controller. My Trimetic panel shows 14.5 volts, but it does not read that extra digit.
I am running the #4 program on the solar charge controller. I believe the absorption set point is 14.4. If I understand the instructions. Gary