just a guess, but if all 4 levelers try and run at the same time and they take 50 amps each, 50 * 4 > 125. You can test for that by only hooking up 1 leveler at a time and see if it still blows the fuse. Plus if one is wired wrong it will help in determining isolating which one.
I would be tempted to wire and fuse each leveler separately.
I would be tempted to wire and fuse each leveler separately.