CATraveler,
I already have a full disconnect switch. This the first time in 13 years there has been an issue.
Once I got to shore power, the inverter/charger started in at 62 amps, after one hour that had risen to 84 amps, in bulk mode. Both those numbers were supplemented by over 10 amps from the solar panels.
After 7 hours that dropped to about 59 amps no longer in bulk mode.
By 11 hours that was down to 10 amps in float mode.
After 15 hours charging is at 1 amp float mode.
The load support is working well, so I'm guessing the battery bank recovered.
I already have a full disconnect switch. This the first time in 13 years there has been an issue.
Once I got to shore power, the inverter/charger started in at 62 amps, after one hour that had risen to 84 amps, in bulk mode. Both those numbers were supplemented by over 10 amps from the solar panels.
After 7 hours that dropped to about 59 amps no longer in bulk mode.
By 11 hours that was down to 10 amps in float mode.
After 15 hours charging is at 1 amp float mode.
The load support is working well, so I'm guessing the battery bank recovered.