dougrainer wrote:
joebedford wrote:
You have 50A service (double breaker in the middle). One of the hots goes to the left breakers and the other goes to the right. Can't imagine any reason other than human error that all the right breakers are off.
Fuse 13 says "waterheat". Your heater needs 12V when running on propane.
Usually, 50 amp supplies every other breaker. Not left and right side
Black hot would be 1-3-5-7-9
Red hot would be 2-4-6-8-10
Black and Red can interchange
In the OP's WFCO, with the 50 amp in the middle it is probably LEFT and RIGHT. Doug
Everyone I've seen in an rv is a split bus, one leg feeds one side and the other leg feeds the other side. Residential/commercial panels do alternate .