time2roll wrote:
Unless there is a propane fueled generator I would not worry about the capacity.
X2!
I would add unless you have a on demand water heater and generator 150K BTU capacity will be more than sufficient.
RV stove 22,000 BTU for top burners, not sure what the oven BTUs are.
34,000 BTU furnace..
6 gallon tank water heater burner 10,000 BTU
All above running at the same time 66,000 BTU.. Well below the capacity of a 150,000 BTU regulator..
On demand tankless water heaters can use as much as 60,000 BTU..