- KpackpackkelleyExplorer IIWhen in doubt call a electrician and it better be a rv electrician not a residential.
- PatJExplorer II
Horsedoc wrote:
Some of these answers are scary.
I agree, which is why I usually sit these threads out. Often the amount of misinformation is stunning. To this particular thread I'll add one thing I don't think has been mentioned in case this comes up in someone's future searches.
If you do decide to add a 240v appliance and have the space for the correct HACR tied breaker, there is one more thing to consider. Some campgrounds have three phase feed, so the 14-50 plug ends up being 120/208, which is allowed and legal. In my experience, many/most newer CG out west with 50A are configured this way. So be sure the "240v" appliance you are installing is also listed for 208v (most mini-splits will be.)
The OP made a good call selecting the 120V unit in my opinion. - HorsedocExplorer IISome of these answers are scary.
- nicpaigeExplorerWell I purchased the 110v unit. Thanks for all the responses. I will update how the install goes and any issues I run into.
- LittleBillExplorer
time2roll wrote:
LittleBill wrote:
I think it is a bit rare actually and certainly not in compliance to NEC.sayoung wrote:
Please explain in detail how on the cheap is done with 50 amp and no 240v, because i don't understand how making it 120v only is easier or cheaper.
As has been said before, lots of " 50 " amp service in campgrounds were installed on the cheap so you will have 120 from ea hot leg to neutral but not 240 hot to hot.
The reports are using a single pole 50a breaker and tie the single hot to both the hot terminals of the outlet. Voila you have "50 amp" service.
that's interesting. Thanks! LittleBill wrote:
I think it is a bit rare actually and certainly not in compliance to NEC.sayoung wrote:
Please explain in detail how on the cheap is done with 50 amp and no 240v, because i don't understand how making it 120v only is easier or cheaper.
As has been said before, lots of " 50 " amp service in campgrounds were installed on the cheap so you will have 120 from ea hot leg to neutral but not 240 hot to hot.
The reports are using a single pole 50a breaker and tie the single hot to both the hot terminals of the outlet. Voila you have "50 amp" service.- LittleBillExplorer
sayoung wrote:
As has been said before, lots of " 50 " amp service in campgrounds were installed on the cheap so you will have 120 from ea hot leg to neutral but not 240 hot to hot.
Please explain in detail how on the cheap is done with 50 amp and no 240v, because i don't understand how making it 120v only is easier or cheaper. - sayoungExplorer
ajriding wrote:
You can if there is 2 phase electricity at the plug (A and B), BUT I think both phases must match, must have the same load on them and the same ability to supply. If it were just you powering off the breaker box then no problem, but who know how many campers are powering off only one phase of the box and not the other? You cannot control that. The first response is saying this, but without much of a warning flag waiving.
Great likelihood of damage to your AC unit. Cheaper to get the 120 version.
As has been said before, lots of " 50 " amp service in campgrounds were installed on the cheap so you will have 120 from ea hot leg to neutral but not 240 hot to hot.
Personally, I only have installed a couple hundred of these units and I haven't seen one that I believe would hold up for the long haul attached to a rv traveling constantly. Others may have a different experience. - ajridingExplorer IIYou can if there is 2 phase electricity at the plug (A and B), BUT I think both phases must match, must have the same load on them and the same ability to supply. If it were just you powering off the breaker box then no problem, but who know how many campers are powering off only one phase of the box and not the other? You cannot control that. The first response is saying this, but without much of a warning flag waiving.
Great likelihood of damage to your AC unit. Cheaper to get the 120 version. - vermilyeExplorerWhile you may need to change the panel or add a sub panel, 240V is available in any normal 50 amp RV service. The biggest problem from my point of view is that you won't be able to run the AC when connected to a 30 amp site using an adapter.
The site wiring that wa8yxm mentioned is rare, but would also present the same problem as using a 30 amp adapter. You need the two legs of 120V, not one leg doubled to get 240V...