time2roll wrote:
if the generator has a single output then yes generator input L1 & L2 will be bonded on the TS.
X2
Generator HOT goes to 'gen input L1' with a jumper from 'gen input L1 to L2'
When generator is source of AC Power.....both L1 & L2 are energized so Main Panel is hot on both busses.
Otherwise only 1/2 of main panel would be hot when on gen.