Keith Haw wrote:
Thanks for the replies. When I use the manual mode it will do the boost and normal but will only blink once for the storage mode. I don't have a good DVM with me so guess I need to pick one up. I usually don't start my generator until the meter I have gets down to 12v so maybe its just not far enough down for boost mode. I can manually switch it to boost but it still never shows over 13.9v to 14.1v. I was just understood that it should charge at 14.4v until it reached 90% then switch to 13.6v. Last night it never got above 13.2v.
Relax, your PD9260 is working just fine. The condition of your batteries has more to do with the current required to charge them (and it's impact/effect on the apparent output voltage) than the charger itself. NO charger can force current into a battery that doesn't require it. The internal resistance of a battery increases with charge and throttles back the current demand. That's what allows the charger to go into float mode.
I suspect that the readings you are seeing has a lot to do with where the readings are taken, sizes and quality of the wiring and the accuracy and sensitivity of your meter.
If your curiosity demands that you see the charge stages progress exactly as the marketing propaganda states, then take an older battery, run it down below 11.5V and hook it (alone) to your 9260. Grab a beer and watch the show.