Toolguy5 wrote:
Sorry to have started this debate.
I now understand why there is so much confusion. The panel in your house the breakers are alternating lines. The panel in the RV is split.
The panel in your house and a 50 amp panel in an RV are
exactly the same except one is rated 50 amps and the one in the house is 200 amps (or possibly 100 amps or other rating). Except for current rating, zero difference. Most breakers are even interchangeable.
Note that the industry standard service voltages are 120 volts and 240 volts, not 110, 115, 117 volts or 220 or 230 volts or any other voltage. Providing that there is no voltage drop on the power company system or the service drop into a house or anywhere downstream of the main panel, the voltages should be 120 and 240 volts with no loads connected/running. An explanation of ANSI standard C84.1 and voltage tolerance boundary can be found
here. Appliances and equipment however can have nameplate voltages other than 120 or 240 volts.
Also, it is incorrect to use the term "phase" when it comes to 120/240 volt services and the designation for each hot leg. The neutral is located exactly 1/2 way between each leg of the 240 volt hot conductors so you get 120 volts in reference to each of the two hot legs. A 120/240 volt service is termed "single phase". "Phase" is a term normally used in 3-phase power systems because there are 3 hot legs each 120 degrees out of phase in reference to the other 2 hot legs (there can be a neutral ("wye")or no neutral ("delta")).
RV parks are occasionally connected to 3-phase systems and have 120/208 volts with 208 volts between the two hot legs. Since most 50 amp RVs don't have 240 volt rated appliances, most will not notice. I'm pretty certain anyone working on any 3-phase derived system has to be a properly licensed electrician, unlike in 120/240 volt CGs where any monkey can work on the systems/components for maintenance.