down home wrote:
Ours lasted 8 years+ One time as far as we know, is all it took. The batteries were dry. We paid for them to be as part of storage to be maintained.
I am concerned about over charging.Currently it is set to float charge at 13.5 volts. As to bulk charging it goes pretty high but I don't remember figures. I have hard getting the controller to do as I understand the manual.
I hope these Folks are familiar with it. If not, a trip to the factory, again.
13.5 float voltage will easily take out FLA by boiling them long term, that is what killed your current FLA.
For best FLA storage, that needs to drop to 13.2V!
According to Battery University, 13.5V-13.8V is supposedly compatible with AGM but with any type of battery that you cannot add water that WILL eventually kill them by either drying them out or eventually warping them. Both results are from overcharging.
Most UPS units are set at 13.8V-14.0V which dramatically shortens the life of AGMs in standby use (typically have to change UPS AGM batteries every 2-3yrs).
I personally use 13.2V for long term float of Gel and AGM batteries for my own designed device use. With that voltage I can easily get 10yrs out of AGMs and Gels.
Once it is fully charged and in storage, there is zero reason to keep hitting AGM, Gel or FLA with anything above 13.2V unless you are equalizing (and that is questionable on AGM or Gel).
Storage mode, you only need to give it enough voltage to "maintain" the full charge, in other words just enough charge to take care of the self discharge. Self discharge on AGMs is much less than FLA so they require far less charging..