ktmrfs wrote:wnjj wrote:
The breakers in the sub panel do not have to add up to the capacity of the supply. Look at your house main panel as an example to see far more than 200A or whatever size panel you have.
Consider too that 50A at 240V is equivalent to 100A at 120V. So you can put several 20A breakers in there and not have an issue even if all were maxed out.
I also see no reason to turn breakers on and off as use them. The 50A breaker at the house will prevent you from overloading the supply.
On final nit pick: You still have a 240V plug in your barn if the RV plug is a 50A one. The RV just uses it as two 50A , 120V circuits.
50A at 240V CAN be UP TO 100A at 120, but could be less, depends on how the two legs are loaded. Each leg is protected to 50A, either leg goes over 50A and a properly installed 50A/240V breaker will trip both legs.
Yeah I left that pesky detail out about balancing them across the legs. As you fill slots in the panel they will alternate so you have to go out of your way to load them all on one side, but your point is taken.