Downsizing to smaller rig, battery capacity

The one I'm looking at holds two standard size 12 volt batteries. I have to run a CPAP @ 3.75 amps and an oxygen concentrator @ 7.9 amps for about 8 hours. I don't know if two standard size batteries could handle this and hoping someone could help me out. Thanks so much, DJ
  • generally it doesn't get below 40 here most times.


    The air going into the CPAP?

    At 54F the heater is at 100% duty
  • Thanks everyone. Guess I will stick with what I have. Just tired of dragging a trailer around. My current set up works good running both machines. Volt meter at 12.9 when I go to bed and 12.4 when I get cup. This is with four Trojan T145's, 450 watts of solar and a couple hours of gen run time for a kick start in the AM.

    I am having trouble with the Xantrex Inverter/charger tho. But I should start a different thread for that.
  • wa8yxm's avatar
    wa8yxm
    Explorer III
    Some "Standard Size" numbers
    GC-2 (six volt you need two in series) about 210-230 amp hours you can safely use half that.

    Group XX.. Most of these are MARINE/deep cycle you should not use more than 25%
    24 about 70-75 AH
    27 just under 100
    29 Just over 100
    31 About 130 I'm guessing you have 27 or 29 as your "Standard"

    A pair of GC-2 would give you more amp hours total and way more usable Amp hours.