Goostoff's avatar
Goostoff
Duo Therm AC freezing up
It happened twice just this weekend and also a once a couple weeks ago. Once I get it thawed out it works fine again. Any idea what to look for as a cause. Neighbor thought maybe refrigerant was low. This is on my 05 Cedar Creek.
  • dougrainer wrote:
    1. They only have 1 lb of coolant, so if you had low coolant, the unit would be TOO LOW on coolant to cool . This is NOT your problem
    2. IF you have a wall tstat, then your unit has a freeze sensor. If you have a freeze sensor, it CANNOT freeze unless the sensor is defective or is NOT installed in the evaporator coils.
    3. IF you have manual roof top Controls, then freezing is a possibility, you need to run on HI Cool and make sure the Evap fins are clean and your Air filter/s are clean. Doug
    Not meaning to argue but low refrigerant will cause freezing coils. AC works by absorbing heat. With low refrigerant ,which results in low pressure it can't absorb enough heat and the coils freeze
  • 1. They only have 1 lb of coolant, so if you had low coolant, the unit would be TOO LOW on coolant to cool . This is NOT your problem
  • Looks like a trip to the roof is in order. Thanks for the replies. I will report back with my findings.
  • Two issues as to why an AC will freeze. Low Coolant, Plugged fins on rooftop unit
  • Have you reviewed placement location of the freeze sensor?
    Access is from the inside.
Having RV issues? Connect with others who have been in your shoes.24,361 PostsLatest Activity: Feb 27, 2026