You state Sub panel. Is this something you or an electrician installed JUST to power your RV? The CORRECT voltage on 50 amp is 120 on EACH Leg. THEN there should be 240 volts when testing between each Leg. IF NOT, you do not have a correctly wired 50 amp sub panel. usually that 70 volts means you have miswired the subpanel and do not have the correct Neutral leg connection. We are assuming that you had NO PROBLEM either at the Dealership or at a Campground with 50 amp service. You just have this problem at your home receptacle. Doug