ktmrfs
Jul 28, 2019Explorer III
dryfly wrote:cavie wrote:road-runner wrote:
There is no issue with using an inverter generator. The issue is with the generator having a floating output as opposed to a bonded neutral. Some non-inverter small generators also have a floating output. When the EMS senses a lack of continunity between the ground and neutral wires, it mis-diagnoses the situation as an open ground. The plug-in outlet testers make the same incorrect diagnosis.
One slight correction. It is diagnosing the situation exactly correct. Open ground. In a main service panel the ground and neutral are bonded together. Every panel after that is a sub-panel and the neutral and grounds are kept separate.
The generator is the Power Company and is the place that the neutral and grounds are bonded. Since the generator is not bonded, the ground is not connected. Think OPEN. Hence the OPEN GROUND indicator. Someday Gen manufacturers are gonna wake up.
This is kinda getting off subject but would you explain why sub-panels should not be bonded? I ran into this issue a couple of years ago when I was installing my whole house generator with automatic transfer switch. I'm obviously not a trained electrician and I'm still having trouble (after a lot of reading and research) in understanding this.
NEC code states that the ground/neutral shall not be bonded downstream of the main panel. It's a safety issue. Also if ground/neutral are bonded downstream of a GFI protector the GFI will trip.
Ground and neutral are NOT the same. one is a return path for the current flowing in the circuit, one is a safety path to earth reference.
Unless there is a fault, no current flows in the ground wire. If ground and neutral are bonded, the current will always flow in the ground wire when something is drawing power. The amount will be shared between the neutral and ground paths.
So in a properly wired trailer ground and neutral should never be bonded since the trailer is intended to be plugged into a pedestal wired to a main panel.
I have used the PI EMS 3A system for a decade. Almost always when running on a generator I dig out my bonding plug. On occasion I've left it somewhere else, in which case I put the PI in the bypass mode.
In reality, the PI and a generator the only likely fault is going to be low or high voltage. not swapped hot/neutral etc.