Expected Amps with MPPT
BlueSky 3000 manual says for a rule of thumb,
"... Ignoring conversion losses the conversion process produces an
output current roughly equal to PV current times the ratio of PV voltage to battery voltage. If a 60 cell module is operating at 25V with 5 amps of output, and battery
voltage was 13V, output charge current from the 3000i would be about 5 amps times 25V ÷ 13V or about 9.6 amps."
I have figures for my 230w panel last summer, where it was operating at 29.3v for Vmp, and output current (calculated using 96% efficiency) was 7.27a and battery voltage was 13.4v (amps to the battery was 15.32 at the time)
So how does that come out using the BlueSky rule of thumb?
7.27 times 29.3/13.4 = 15.9a (without conversion losses) and I got 15.32.
So that seems to work! It does not tell you what happens with higher panel temps when power drops off.
Another set of numbers from real life with hot panel.
MPPT is still holding at 29.3vmp but now power was less so output current was 6.47 (calculated) battery 13.2v
6.47 times 29.3/13.2 = 14.36a I got 13.88a to the battery
So my conversion loss was 15.9-15.32 =0.58 from 15.9 = 3.6 and
14.36-13.88 = 0.48 of 14.36 = 3.3 so in ball park for in-the-field measuring. My est of 96% leaves 4 so 3.6 is reasonable.
EDIT--Maybe I counted the loss twice? I already used 96% controller efficiency to calculate the panel amps output. (Estimating controller output watts as seen on display is 96%, get input watts, divide by Vmp to get calculated amps)
With higher panel temps Isc goes up, but with MPPT buck conversion, Isc means nothing. Amps is only from watts/volts. So panel output amps drop with panel power while Vmp stays the same (it appears!)
Didn't know that. Maybe it's wrong. The trouble is I have no ammeter on that panel output. Only know the controller output watts and panel volts with an assumed efficiency percentage. Got to get an ammeter on that line to confirm calculation, but it does seem to come out fairly close as is.
without knowing any of that stuff, my other way to get "expected amps" is just to take what PWM should get and add say 8% for MPPT but that only works for a cold panel.
eg that 230w with MPPT above with 15.3a actual to the battery.
PWM means 130w Isc 8.2a so 230/130 x 8.2= 14.5a Add 8% (1.16a) for MPPT = 15.66. So you can get somewhere close that way, but only for a cold panel (and panels get hot!)
"... Ignoring conversion losses the conversion process produces an
output current roughly equal to PV current times the ratio of PV voltage to battery voltage. If a 60 cell module is operating at 25V with 5 amps of output, and battery
voltage was 13V, output charge current from the 3000i would be about 5 amps times 25V ÷ 13V or about 9.6 amps."
I have figures for my 230w panel last summer, where it was operating at 29.3v for Vmp, and output current (calculated using 96% efficiency) was 7.27a and battery voltage was 13.4v (amps to the battery was 15.32 at the time)
So how does that come out using the BlueSky rule of thumb?
7.27 times 29.3/13.4 = 15.9a (without conversion losses) and I got 15.32.
So that seems to work! It does not tell you what happens with higher panel temps when power drops off.
Another set of numbers from real life with hot panel.
MPPT is still holding at 29.3vmp but now power was less so output current was 6.47 (calculated) battery 13.2v
6.47 times 29.3/13.2 = 14.36a I got 13.88a to the battery
So my conversion loss was 15.9-15.32 =0.58 from 15.9 = 3.6 and
14.36-13.88 = 0.48 of 14.36 = 3.3 so in ball park for in-the-field measuring. My est of 96% leaves 4 so 3.6 is reasonable.
EDIT--Maybe I counted the loss twice? I already used 96% controller efficiency to calculate the panel amps output. (Estimating controller output watts as seen on display is 96%, get input watts, divide by Vmp to get calculated amps)
With higher panel temps Isc goes up, but with MPPT buck conversion, Isc means nothing. Amps is only from watts/volts. So panel output amps drop with panel power while Vmp stays the same (it appears!)
Didn't know that. Maybe it's wrong. The trouble is I have no ammeter on that panel output. Only know the controller output watts and panel volts with an assumed efficiency percentage. Got to get an ammeter on that line to confirm calculation, but it does seem to come out fairly close as is.
without knowing any of that stuff, my other way to get "expected amps" is just to take what PWM should get and add say 8% for MPPT but that only works for a cold panel.
eg that 230w with MPPT above with 15.3a actual to the battery.
PWM means 130w Isc 8.2a so 230/130 x 8.2= 14.5a Add 8% (1.16a) for MPPT = 15.66. So you can get somewhere close that way, but only for a cold panel (and panels get hot!)