I understand that my Honda 2000i has a floating neutral and my Progressive Ind. PT30C sees that as a fault. I've been able to get around that by using a neutral/ground bond plug. My question(without...
One will be fine as long as it's on the one the cord is plugged into. There's no ground connection from the RV plug to the paralleled generator. There's only a ground connection to the one it's plugged into.
EDIT: Bad info from me. If the parallel cable ground is connected, the bond plug can be on either. Thanks ktmrfs.