Bob E. wrote:
Thanks guys! These photos and information have been very helpful. I ordered the newer gas valve (#31098) because it looks like it has the gas inlet and outlet ports in the correct place (or at least close to it). Supposed to be delivered Thursday. I'll let you know if it works when I get a chance to mess with it...hopefully this weekend. If not, I may have to go with the 31150 and try to find that L-shaped tube on the outlet side. Otherwise, I don't think I will have enough room at the bottom of the valve to connect the gas line on the inlet side.
Hey guys just wanted to drop in here and thank everyone for this thread. I have the hydroflame 8531-iii and encountered the exact same problem of not being able to find the Atwood 31155 gas valve because, well, they just don't make them anymore.
So, even though I didn't know the results for Bob, I took the plunge and ordered the
Dometic 31908 from Amazon as suggested, and it worked!
BUT... it's never that easy, right? It took several hours of trying different things and head scratching, but eventually I got it to work by installing it sideways with the input port pointing UP (solenoids on the left, touching the fan housing), and drilling a hole in the top sheet metal to bring in the gas line from above. Additionally, I had to move not just the orifice over from the old valve, but the orifice AND the carrier "tube". Mercifully, the threaded outlet port on the 31908 is 3/8" npt thread, just the same as the 31155, so no adapter required. I had to do this to provide enough clearance to plug the ignitor wire in.
Now, if drilling a new hole is absolutely out of the question for you, I think it WOULD be possible to very creatively use brass elbows and pipe nipples to get the input where you can use the existing side entrance setup. My GUESS is you'd probably want a 3/8" female flare to 1/4" female npt elbow, a couple of 1/4" street elbows, a 2" nipple (or maybe 1.5"?), and finally a female 1/4" npt to 3/8" male flare elbow. Alternatively, you might also be able to use a 3/8" flare street (swivel) elbow and a short piece of rubber/flexible propane hose - although with the exhaust pipe running through the same space I wouldn't take that kind of risk. Note that the inlet in this configuration is maybe an inch from the top sheet metal, so if you put an elbow on it will be touching the "ceiling" - not much room!
For me, just cutting the hole in the ceiling made the most sense. It was the least expensive option and I just sort of stuffed some fiberglass insulation around the copper line once the flare nut was poked through. The furnace is very old and I just need it to work. The RV is also old and doesn't move (much), so I'm not worried about rubbing. You might decide to install some sort of grommet if you're going to be moving.
Finally I might also note that there is a stamped bracket on the original valve that helps attach it to the fan housing, giving the whole works a little more rigidity. My furnace no longer has that feature due to the completely different valve and configuration.
Anyway, thanks again, especially to BFL13 who made the suggestion. I have heat now, which is what matters!
EDIT: Here's what it looks like installed...