Furnace runs for 8 minutes at a time.

This is driving me nuts. For the past few months, my furnace has adopted this annoying feature in that it only runs for eight minutes at a time. To make it run more, you have to turn the thermostat DOWN (where it will then make that "click" sound) and then back up, or turn it off and back on. If you leave it alone, it will come back on in one hour and run for another eight minutes.

The furnace is a Suburban NP-30 if I remember the model correctly. Over the last 2-1/2 years it's been totally rebuilt. It has a new thermostat, new board (Dinosaur board), new sail switch, new motor, and new gas valve. Oh and a new limit switch.

A friend who works on RVs first said it's probably the limit switch. So at his recommendation, I removed it and jumpered across it to eliminate that as a possibility. Nope, didn't fix anything.

Next, we replaced the circuit board again... it already had a Dinosaur board, and that board even passed his board tester, but we put a new one in it just because. Again, no change.

Yesterday, I replaced the wall thermostat. And, still no change.

I'm running out of ideas... so thought I'd post here. I'm leaving for a trip in less than a week and I'll be dry camping for two weeks... I sure would like to have a working furnace!!

Rob

18 Replies

  • It sounds like there is an imbalance in the warm air around the thermostat. Is it possible that there is a heater vent blowing toward the area of the thermostat heating up that area faster than the rest of the trailer causing the thermostat to kick off early?

    If so you might try setting a fan in that area to circulate the warmer air away, or partially closing off heater vents nearest the thermostat.

    If you completely close off a vent it may cause the limit switch to overheat.
  • RobG wrote:
    The whole furnace shuts off after 8 minutes.

    Fan control board ? Um... other than the Dinosaur board, no idea. I know there's a connection on it for the Blower.

    It's an NT-30SP now that you mention it.

    The box the board came in says FAN50PLUS. This is the same board that's been in it for two years and it was working fine until recently.


    OK- that is all good. Does it actually light? The eight minutes is about the time a fan control board (the Fan50Plus) will run before shutting down if the flame is not sensed. If the burner is igniting and burning well, and you can see the electrode is in the flame, I would do a continuity test on the ignition wire and electrode. There can be a break in one or the other, and the spark will jump it, but it will not pass the current needed to sense the flame.
    If the flame is not good, look at LP pressure, etc.
  • Sounds like the thermostat tolerance is too wide. Might be something like +/- 2 degrees default. What thermostat did you install? The tolerance may be adjustable.

    Ex. In heating set to 70 degrees. Furnace comes on when temp drops below 68 then shuts off at 72. Will not come on again until temp drops below 68 again. When you lower the temperature setting manually you are resetting the thermostat and that's why it starts again.
  • The whole furnace shuts off after 8 minutes.

    Fan control board ? Um... other than the Dinosaur board, no idea. I know there's a connection on it for the Blower.

    It's an NT-30SP now that you mention it.

    The box the board came in says FAN50PLUS. This is the same board that's been in it for two years and it was working fine until recently.
  • Is the blower stopping, or just the flame?
    Does it have a fan control board?
    If it does, is that the original, or was it retrofitted with the Dinosaur Fan Control 50?
    Last, is it an SF-30 or NT-30SP?
  • That would be the job of the Limit switch.. which has been removed.

    Besides, the thing has been out and apart so many times, it's clean. I'm sure of it.
  • The furnace could need a good cleaning. It is possible that the high temperature cut out is turning the furnace off rather then the thermostat reaching temperature.