- MEXICOWANDERERExplorerIt's when the controller throws a hissy-fit and holds it's breath until it passes out that a fuse comes into play. This is far less common than a fault between the battery and the controller.
Visit the area in an OEM plant. It's sounds like WW 3 staple gun warfare. Now imagine a big panel staple ALMOST shorting a hot wire. It works until it's bounded down the highway a few thousand miles.
Myself I am old fashioned. I put the panels to sleep before working on the system. A tarp or towels. - Rail_DawgExplorer
2oldman wrote:
time2roll wrote:
x2. I don't really see a need to fuse any of it. So I don't.
As long as the ampacity of the wire from the panels to the controller exceeds the Isc rating of the panels... no fuse is needed.
Hmm good point. - HoustedExplorer IIII fuse both into and out of controller as a convenient way to disconnect for service.
JMHO
Housted - 2oldmanExplorer II
time2roll wrote:
x2. I don't really see a need to fuse any of it. So I don't.
As long as the ampacity of the wire from the panels to the controller exceeds the Isc rating of the panels... no fuse is needed. Rail Dawg wrote:
As long as the ampacity of the wire from the panels to the controller exceeds the Isc rating of the panels... no fuse is needed. You can short the wires all day long with no harm to the wire or panels. A DC rated switch might prove useful to cut power to the controller for service. Most controllers need the solar power disconnected before disconnecting from the battery. Or you can remove that fuse.
I’ll fuse at 30 amps between the solar and controller.
There’s also a 30-amp fuse at the battery installed by the manufacturer.
Do appreciate the input!- Rail_DawgExplorerI’ll fuse at 30 amps between the solar and controller.
There’s also a 30-amp fuse at the battery installed by the manufacturer.
Do appreciate the input! - scrubjaysnestExplorer
time2roll wrote:
Morningstar says to comply with NEC the fuse (battery to controller) s/b rated at least 20% over the controller rating and wire should have ampacity to match the fuse. So you are looking at 40 amp fuse and #8 wire minimum afaik. Fuse s/b close to the battery not the controller. If you are pushing near 30 amps I would have #6 wire minimum assuming wire fits the controller lugs.
The problem with the NEC on this is the rules apply to grid tie systems which RV's are not. I chose a breaker at the batteries to protect the wire and then another breaker at the CC to protect the electronics.
Just a different approach. - brulazExplorerFuse to protect the wire first, then reduce that fuse rating to protect the electronics second.
So if your wire can handle 40A but your electronics only 30A, go with a 30A fuse. - morphriderExplorer
- morphriderExplorerRead Renogy site about fusing. Match the controller, seems if you went a size larger than controller then you risk ruining the controller. Makes no sense to go that 20% higher that windynation refers to. I think that 20% reference goes from the solar panels to the controller, not from controller to battery. Read the clicky below...