Generator struggles to start A/C

This season I am having issues with my Honda EU3000i handi generator starting the A/C compressor. It has worked fine the last 7 years, even using the Eco throttle setting (low idle) at 115+* heat or at 8000’ elevation.
A/C is a Dometic 13.5K BTU unit from 2003. On shore power (dedicated 20A) it starts fine within 1 second, drawing about 20A max
On the generator (in Eco mode), using a 30A twistlock adapter, the generator boggs down and the overload protection on the compressor actives, then tries again and will usually start and run compressor. If I disable the Eco feature and let it run at a higher RPM, it will start A/C but goes to locked rotor current for a second or 2.
So I bought a hard start kit and took some measurement before and after. This unit already had one, so I left it and installed the new one in parallel. There was no change in performance, so the old one is likely OK.
Min voltage = 58 Volts. (!?!)
Max current = 56 amps (RLA is 59A)
So the generator still produces 3kw as it is rated but the low voltage is not tolerated by the A/C.
So given the A/C starts nice and quick (even after a short cycle) on shore power, I suspect the generator. I serviced the air filter, spark arrestor, spark plug and changed the oil. All was well before so no change after this. Unit blinks twice so about 200 hrs on it. Runs fine at idle and full load. Starts on 1st pull as always.
So it appears the generator has a load transient issue that it did not have before. Under stead state conditions with A/C running, output is right at 120V drawing 12A, like it should.

What to do next?