Originally, I posted this:
Bobbo wrote:
These are both wrong. Turning off the breaker, by itself, will not do anything to diagnose the problem. The problem is a short between GROUND and a NEUTRAL, and the breakers do not affect that.
You MUST disconnect all of the NEUTRAL wires from the NEUTRAL buss bar to diagnose this. Only with every NEUTRAL disconnected can you know if it is between the breaker box and the Surge Guard.
Bobbo is 100% correct. His procedure will lead you to the problem. The only thing I'd add is that it may be difficult to disconnect all the neutrals, so when tracking this down, I start by unplugging devices that will unplug (the problem could be in something plugged in) and then I remove neutrals from the most likely suspects - outside sockets, water heater, etc. If that doesn't do it, I remove half the neutrals, test, then the other half.
Then I saw this post and decided more info was needed:
Sorry, but if there is NO Black 120 power, then the GFCI will not trip if the short is downstream from the breaker panel. If the CG GFCI trips with the Main RV breakers OFF, the problem is BEFORE the breaker panel in the RV. The fact he has a Surge Guard means he needs to bypass it and then see. I have 34 years as a Tech and have diagnoised (and fixed) dozens of these type issues over the years, and what I posted is the BEST way to determine where the problem is located and to start. A GFCI will NOT trip if it does NOT have Black Hot power. Just having a Neutral and a Ground (and a short/imbalance) will not cause a GFCI to trip.
Bobbo is right. A modern GFCI will trip even if there's no power on the hot lead. Many of us were taught that the GFCI compares the current going through the hot lead with the return current through the neutral and would trip if they aren't the same. Older GFCI's did that, so if there was no hot current, it wouldn't trip. Newer GFCIs are smarter and will trip if there's no load. You can try it. Stick some wire into neutral and ground on a GFCI socket and the GFCI trips. I've done it. That's what happens. If you do it, make sure you know what's neutral and what's hot !!!!!
I wondered why and got this answer:
"GFCIs contain a second toroid coil which induces a small current in the H and N wires at 120Hz. If the N and G are touching on the load side of the GFCI, there is current flow back through the main panel N-G connection; the sensing coil recognizes this as an imbalance between the H and N and trips the device. "
So, Bobbo is right. You have to disconnect the neutrals (or unplug devices, which disconnects the neutral at the plug). Turning off breakers tells you almost nothing.