Harvard
Apr 17, 2018Explorer
road-runner wrote:Harvard wrote:Just for debate's sake, if the stray capacitance were balanced, there would be equal leakage between hot-ground and neutral-ground. Exaggerated, you could leak a full amp on both sides and not trip the GFCI. As I type this, I'm agreeing with you more and more, because I've never seen the leakage to be exactly equal, with more being ground-neutral than ground-hot. So agreeing with you, I'd place my bets on the imbalance being heavier between neutral and ground.
Personally, I would suspect the GCFI to be faulty IF IT DID NOT trip with the 3 RVs. But then that is just me and my stray capacitance theories. :)
Yes, the stray C is balanced BUT the VAC across the two is very different. The HOT wire is 120 VAC to GROUND while the NEUTRAL is almost 0.0 VAC to GROUND. Which one is going to have the most leakage current? The HOT, IMO.
Having RV issues? Connect with others who have been in your shoes.24,409 PostsLatest Activity: Aug 23, 2026