dougrainer wrote:Yes mine did this. Fan would run continuous but if you really paid attention the burner would cycle on and off every 30 to 90 seconds.
If you have a blockage, the furnace burner would short cycle and you would hear it cut on and off. Doug
My ducting had a few issues. First the short section from furnace to main line protruded 40% into the main line and blocked airflow. Secondly the short section collapsed during installation and was restricted. Flashlight and mirror found these issues.
Used a hole saw to open the metal protruding into the main line. Used some square aluminum that I perforated for air flow as a scaffold to prop open the collapsed section.
Helped some but the real solution was to pop out two of those knock-outs and add two more 4" ducts direct to the living area. Now I get tons of massive heat compared to before. Burner runs continuous until heat gets to the thermostat. Far less furnace fan run time.