Home plug-in options?

When my 30 amp FW is at home, I have two electrical options. I can plug in close with a 25' 12 ga cord, into a 15 amp circuit.

I also have a 30amp circuit, just for a rarely used air comp. It would require a 50' 12 ga cord to reach.

I have a 30 to 15 amp 6" dogbone, that I use to hookup.

My question is, will I get much more amperage from the further away 30 amp circuit, than the closer 15 amp, since I still need the 30-15 dog bone to hook up?

Will I only get 15 amps no matter what, since the dogbone is reducing to 15 amps?

I would appeciate any help or thoughts.

Jerry

13 Replies

  • The electrician made an error when he used 12 AWG wire and a duplex outlet for a 30amp circuit. 30 amps requires 10 AWG wire minimum for a 30 amp circuit.

    Here are the wiring requirements:

    15amp - 14 AWG
    20amp - 12 AWG
    30amp - 10 AWG

    Also, a 30 amp circuit requires a different receptacle compared to your normal 15/20 amp duplex receptacle.

    If it were me, I'd connect a new 30amp breaker, 10 AWG wire and dedicated 30amp outlet for the RV, and I'd replace the 12 AWG wire and duplex outlet for the compresser.
  • The 30 amp circuit is 110/120. It is a 30 amp breaker in my home entrance, that is wired just a short distance to my compressor, with a normal 2 outlet plug in.

    The electrician just used a 12 ga wire to the outlet, about 10 feet.

    Is there a heavier dogbone that I could buy, such as 30-30 or 30-20? I have only seen the 30-15.

    I normally just plug in for charging the battery, and using the fridge on electric, when getting ready to go camping, otherwise I'd consider putting in a proper RV outlet.

    Thanks for your reply pianotuna!

    Jerry
  • Hi Jerry,

    The dogbone won't reduce the amperage--but it is probably rated for 15 amps. If you use it for more than a short time at a 30 amp draw it may melt.

    A #12 cord is limited to 20 amps.

    Are you certain the 30 amp circuit is 110 volts?

    If so, make up a #10 cord and perhaps add a proper 30 amp outlet to the air compressor.