Huntindog wrote:
2oldman wrote:
Huntindog wrote:
banana plug cords tapped in before the 20 amp breaker will allow for higher output. Correct?
Since the rated output is 13.3a, I'm not sure what you're getting at. You mean a surge current?
No.If I understood SoundGuy right, it is possible to twin the honda's by making a suicide cord (two male 110 electrical cord) and pluging each end into a receptacle of the hondas... Doing this would tap the power AFTER the 20 amp breaker. twining the normal way with the banana plug cords taps the power BEFORE the circuit breaker.
You understand correct about the paralleling, however there is no "higher output" to be had. Each generator limits out at less than 20A anyway sharing before or after the 20A breaker makes no power difference.
Honda parallels them behind the breaker because they don't want someone trying to pull 26A from the 20A receptacle on the non-companion model.
Correction: simply connecting the Hondas with a suicide cord doesn't work because there isn't a 30A receptacle. I think what people do is build a Y cable with 2 male 15A plugs and a female 30A receptacle. Simply suicide connecting the generators means you still don't have anywhere to plug in something more than 20A.