Some thoughts.
Yes the Honda 2000i regular outlet is rated for 20amps.
The plug 99% of the people use to plug into it is only rated for 15 amps (even if the cord is 12 gauge and rated for 20 amps).
While the generator can produce 18 amps
See the issue?
You can have a real problem drawing more current through the plug (NEMA 5-15) (and maybe cord) then it is rated for.
Personally I would get the Companion